I have been told by inspectors in residential situations that if we ground the rebar in the slab that ground rods are not required. I thought that the code required any available electrode to be installed if available. Thoughts?
Your inspector is correct. Look at art. 250.53(D)(2). It basically states that we must augment the underground water pipe with any of the electrodes in 250.52(A)(2) thru A(8).I have been told by inspectors in residential situations that if we ground the rebar in the slab that ground rods are not required. I thought that the code required any available electrode to be installed if available. Thoughts?
In this area some POCOs require a ground rod regardless.
Something you might keep in mind.
I just had one of my new construction guys call and said he was turned down for a fire pump install, he did not install or connect to a grounding electrode for the fire pump service. (he should have known better anyway, he has a masters license, and of course the engineer that drawed the blueprints didn't know any better either, because he left it off) When he asked the inspector if the exsisting cold water and building steel (commercial building)was Ok, the inspector said he wanted a ground rod too. I told him to politely ask the inspector where in the code he was required to also drive a ground rod when the other two grounding electrodes were present.
I might stutter a bit when asked the same question because the thought would be running through my mind "Does that building steel actually qualify as a grounding electrode in this case?"The inspector stuttered when he said it, so I figured he was not sure and defaulted back to one of those "that's the way it's always been done around here."![]()
In the 2008 code, I believe the code reference might be 250.52(A)(2)
250.52(A)(2)
"
Well, that is one way to satisfy code. The other is to use a CEE- rebar electrode- in that cas no rods are needed. There are also other means but generally these are the most common.In this case the water pipe is not an available electrode. So if I understand it correctly since the water pipe is not available a rod must be driven?