captainwireman
Senior Member
- Location
- USA, mostly.
Health Care facilities
Health Care facilities
The 2011 NEC includes health care facilities including nursing homes, clinics, dental and medical offices among others too. This is a 2 part grounding system complying with 250.118 and 517.13 (B) which specifies an insulated grounding conductor must be run with the branch circuit conductors in accordance with 517.13 (A).
It is important to note that a bare grounding conductor in conduit or tubing is just a parallel ground, not a seperate one.
Health Care facilities
I believe it is an insulated grounding conductor properly identified shall be ran in a metallic conduit that qualifies as a redundant EGC for 517 installs.
The 2011 NEC includes health care facilities including nursing homes, clinics, dental and medical offices among others too. This is a 2 part grounding system complying with 250.118 and 517.13 (B) which specifies an insulated grounding conductor must be run with the branch circuit conductors in accordance with 517.13 (A).
It is important to note that a bare grounding conductor in conduit or tubing is just a parallel ground, not a seperate one.