Grounding Flammables Cabinet

jmellc

Senior Member
Location
Durham, NC
Occupation
Facility Maintenance Tech. Licensed Electrician
I've seen flam cabinets grounded to building steel, probably the best method. Also seen them grounded to the concrete floor and equipment stands. I would think concrete floor is OK, as the main issue is preventing static shocks from cabinet to floor. Equipment stands don't seem like a good option as they may be moved and ground ignored or not noticed by some laymen. I can't find much in code about it.

What say you guys here?
 
I see no need to bond the storage cabinet, even though everyone I have seen has a grounding lug. I took a quick look at NFPA 30 and did not find a bonding or grounding requirement for the cabinet
 