Hello everyone,
I have a scenario on a project that we can't seem to agree on and would like your input.
I have a 480 volt, 1140amp circuit that is coming out of our MDP that is feeding a load a few hundred feet away.
It is being paralleled 3 times with 500MCM tray cable. It goes from 3 conduits, one per parallel, to cable tray back the to 3 conduits at the load end.
The question is, do we have run three separate 3/0 grounds or could we run one 3/0 in the tray and tap it at the ends for the conduit?