Expanding somewhat on my original question one of the feeders from this new Switchboard feeds a large chiller and auxiliary chiller pumps located on a new concrete pad some distance away.
I'm also trying to determine weather or not this new Chiller location requires a Grounding Electrode System per 250.32? Here's what I'm considering to make the determination:
1) Would this new chiller pad and equipment be considered a building or structure?
2) Is the circuit to the chiller considered a feeder ( or is this a branch circuit)? I would think its a branch circuit fed from the upstream switchboard since it only feeds a chiller starter. But what if inside the chiller enclosure there was other small distribution components that had further branch circuits to the individual chiller components?
If the answer is no to either of the above then I take it that a GES is not required? However would it be good practice to still install a ground rod, CEE, ground ring, etc....? I see lots of industrial designs that appear to have ground rings at locations like this weather its required or not.