Installed a 250kw diesel generator, engineer called for 2/0 for grounding electrode. Electrical Inspector failed it because he said it must be a 3/0 because the line side of the main disconnect is 3 sets of 400‘s as per 250.66. I agree with the inspector but the engineer is pushing back saying that is not the way to figure ground size for generator, can someone please tell me where to find the the proper grounding size, thanks