grounding generator

Status
Not open for further replies.

mark m.

Member
Location
New Jersey
I, RECENTLY INSTALLED THE WIRING FOR MOBILE GENERATOR. THE GENERATOR FED A 3 PHASE 4000A MAIN BREAKER THAT IS ALSO LOCATED INSIDE THE MOBILE CONTAINER.WE FED FROM THE GEN TO THE BREAKER W/ (6)-535 RHW (LOCOMOTIVE WIRE) PER PHASE & NUETRAL.
MY QUESTION IS ABOUT THE GRD. DO I SIZE IT ACCORDING TO SIZE OF THE FEEDERS(4-3 0) OR DO I SIZE IT TO SIZE OF THE BREAKER(500MCM)?
 

dereckbc

Moderator
Staff member
Location
Plano, TX
Re: grounding generator

Depends on if the genset is SDS or not. SDS requires a GEC and EGC's. GEC sized per 250.66, EGC's sized per 250.122

Genset is not SDS only EGC sized per 250.122

Please turn off the CAPS
 