grounding generator

Status
Not open for further replies.

mark m.

Member
Location
New Jersey
I, RECENTLY INSTALLED THE WIRING FOR MOBILE GENERATOR. THE GENERATOR FED A 3 PHASE 4000A MAIN BREAKER THAT IS ALSO LOCATED INSIDE THE MOBILE CONTAINER.WE FED FROM THE GEN TO THE BREAKER W/ (6)-535 RHW (LOCOMOTIVE WIRE) PER PHASE & NUETRAL.
MY QUESTION IS ABOUT THE GRD. DO I SIZE IT ACCORDING TO SIZE OF THE FEEDERS(4-3 0) OR DO I SIZE IT TO SIZE OF THE BREAKER(500MCM)?
 
Re: grounding generator

Depends on if the genset is SDS or not. SDS requires a GEC and EGC's. GEC sized per 250.66, EGC's sized per 250.122

Genset is not SDS only EGC sized per 250.122

Please turn off the CAPS
 
Status
Not open for further replies.
Top