First time poster, long time lurker
I have a site that has a grounding potental problem. First a brief overiew of the site.
(1) property aprox 300 feet deep
(2) front property line is a road
(3) rear property line is a rail road with DC tracton supply 3rd rail that also has the local POCO high voltage feeds to the substations overhead.
Located on a concrete pad aprox 50 feet from the railroad and 40 feet from the POCO overhead we have a 8 X 40 foot steel fire training trailer.
Service is from a pole mounted service located at the road, the service has 2 rods and the ground is bonded to neutral at the service. From the service there is aprox 200 feet of #6 (trailer needs 22A, #6 is for voltage drop) 4 wire (2hot 1 neutral 1 ground) It terminates at the trailer in a "mobile home" pedastal 4 wire and the trailer plugs in from there. In the trailer the neutral and ground are seperated as the service is already bonded once.
At the trailer today in the pouring rain there was a complaint of a slight tingle between an aluminum ladder that was in a puddle of water and the roof of the trailer (ladder was insulated from trailer by a thick coating of paint)
I took voltage readings with a fluke DVOM and got 9 volts AC. Looked at the grounds and they are all good, ground to neutral is in the MV range. Decided to drive a ground rod and bond it to the trailer frame, it made very little differance.
I started to take some readings between the puddles on the ground and the trailer frame. At the front I got 5 volts, middle of trailer 9 volts and at the rear (the end closest to the RR and POCO)13 volts. I opened the service disconnect to the site (200 feet away) and there was no change at all in the readings.
I am thinking that this site needs to be excavited for at least 4 feet all the way around the trailer slab and a grounding grid constructed and bonded to the trailer. Kind of like a in ground pool.
What do you guys think, I need to dry out and think about this some more.
I have a site that has a grounding potental problem. First a brief overiew of the site.
(1) property aprox 300 feet deep
(2) front property line is a road
(3) rear property line is a rail road with DC tracton supply 3rd rail that also has the local POCO high voltage feeds to the substations overhead.
Located on a concrete pad aprox 50 feet from the railroad and 40 feet from the POCO overhead we have a 8 X 40 foot steel fire training trailer.
Service is from a pole mounted service located at the road, the service has 2 rods and the ground is bonded to neutral at the service. From the service there is aprox 200 feet of #6 (trailer needs 22A, #6 is for voltage drop) 4 wire (2hot 1 neutral 1 ground) It terminates at the trailer in a "mobile home" pedastal 4 wire and the trailer plugs in from there. In the trailer the neutral and ground are seperated as the service is already bonded once.
At the trailer today in the pouring rain there was a complaint of a slight tingle between an aluminum ladder that was in a puddle of water and the roof of the trailer (ladder was insulated from trailer by a thick coating of paint)
I took voltage readings with a fluke DVOM and got 9 volts AC. Looked at the grounds and they are all good, ground to neutral is in the MV range. Decided to drive a ground rod and bond it to the trailer frame, it made very little differance.
I started to take some readings between the puddles on the ground and the trailer frame. At the front I got 5 volts, middle of trailer 9 volts and at the rear (the end closest to the RR and POCO)13 volts. I opened the service disconnect to the site (200 feet away) and there was no change at all in the readings.
I am thinking that this site needs to be excavited for at least 4 feet all the way around the trailer slab and a grounding grid constructed and bonded to the trailer. Kind of like a in ground pool.
What do you guys think, I need to dry out and think about this some more.