1972Grady
Member
- Location
- Tampa Fl USA
Sorry. I didn't read what I posted for #2. Correct. The smallest OCP you could feed from a 4000A busway protected at 4000A would be 400A. There is only 1 Grady. It depends which computer I log in with as to which name populates.250 KCMIL AL is rated for 205A in the 75C column. I have 2 sets of them so that puts me at 410 amps which is greater than the 10% rule in 240.21(B)(1)(4)