Good day ,
As per NEC 350.60 ,Where used to connect equipment where flexibility is required after installation, an equipment grounding conductor shall be installed. Is grounding of LFMC both ends required if it runs between two non-metallic enclosures ( GRP or Glass Reinforced Plastic) ? Is NEC 250.134 applicable in this situation ( isolated raceway) .
Note that LT connector is PVC coated . The system voltage is 24 Vdc , Load is 2.5 Amps and enclosures are mounted on steel structural which is already grounded .
As per NEC 350.60 ,Where used to connect equipment where flexibility is required after installation, an equipment grounding conductor shall be installed. Is grounding of LFMC both ends required if it runs between two non-metallic enclosures ( GRP or Glass Reinforced Plastic) ? Is NEC 250.134 applicable in this situation ( isolated raceway) .