Hello............
Is this correct?
I've always favored this EGC routing as shown in the photo, as, in my opinion, less box volume is used up and the routing of the EGC is a little more controlled.
free conductor is not spliced -- as long as 6" of continuous conductor exist for terminations or splicing
free conductor is not spliced -- as long as 6" of continuous conductor exist for terminations or splicing
That word "free" has me.......
if the ground is clamped down by that screw as in the picture, it is not free (https://www.youtube.com/watch?v=lLCEUpIg8rE) 6" from where it emerges from the sheath.. I would think??
I do prefer as mentioned doing as pictured, but since the comment from the instructor/inspector, I now leave the length..
Are you saying you have 6" of bare wire before it reaches the ground screw? I can't believe that was the intent.
Most overlook the fact that unless a box is 8" or more in any direction, then you don't need 6". You only have to have wire long enough to extend 3" outside the opening.
300.14
I know that is a common read of that section but I am not sure I agree that is what the NEC requires.
Let's say a wire comes up short, say a drywall guy hit it with the router leaving only 2" of conductor. That would be a violation.
Now I come to put the device in place so I butt splice more conductor onto that 2" conductor resulting in 6" of free conductor.
In my opinion my repair removes the violation.
Are you implying that any spliced conductor could be 2" as long as the pigtail is 6"?
emerges from the sheath & the continuous comment is based on the lenght after ground screw.