John120/240
Senior Member
- Location
- Olathe, Kansas
ritelec your install looks good. 1/4" min to 3/4" max of romex jacket in the box. I would have 6" of conductor after bonding the box.
No, but there is a rule that says that the screw for the EGC can't be used for any thing else. Your out of luck. Sorry that there's no good news for right now.Does this rule make it illegal to wrap the ground around the end of the sheathing and clamp it into a metal romex connector? I find that method in old remodels all the time and it would be really handy when wiring toe-kick heaters with their ridiculous ground-clamp.
No, but there is a rule that says that the screw for the EGC can't be used for any thing else. Your out of luck. Sorry that there's no good news for right now.
Something like thatso install one rx connector for the nm wire.............. and another rx connector just for the ground........
True you only count them as one when it comes to calculations, but if you put 40 EGC jumpers in one box that don't leave the box they still count as one - but good luck pushing them all in and getting a device or cover on the box.E.G's defy the laws of physics. If they are all the same size they only count as one.........![]()
so install one rx connector for the nm wire.............. and another rx connector just for the ground........
No, but there is a rule that says that the screw for the EGC can't be used for any thing else. Your out of luck. Sorry that there's no good news for right now.
Are you suggesting using the clamp screw for an unused clamp for attaching a grounding conductor to the box?I wouldn't be using it for anything else. Just leaving it empty.
I've heard about this "bonding method" mostly here on the Forum. . . never seen it in the wild. What I recall is that the practice of squeezing a romex EGC between the romex sheath and the jaw of a metal two-screw romex clamp (or the internal metal box clamp) was occasionally allowed by a local AHJ in the initial years of figuring out how to wire that new-fangled Romex With Ground. -- The 1960s.Does this rule make it illegal to wrap the ground around the end of the sheathing and clamp it into a metal romex connector?
some used to wrap the EGC around the screw that is also the clamping method for the clamp - . . .