A building is wired using EMT conduit from the panelboard to each receptacle box and an equipment grounding conductor is also installed. Article 250.148 (C) requires the equipment grounding conductor to be connected to the metal box by means of a grounding screw or a listed grounding device. Contractor installed self grounding receptacles and connected the grounding conductor to the receptacle, not the box. Does this meet code.