Situation: Single phase residential 120/240v, 200a underground service with the meter socket on a post in the yard. The poco and customers neutral conductors are bonded to the meter enclosure. 3 conductor underground service lateral to the main breaker in a residential panelboard. #4 bare GEC from panelboard to the concrete encased electrode in footer.
Question: Would any interpretation of the NEC require a rod to be driven at the meter socket?
Poco is not presently requiring this but the AHJ is and I can't find any local requirement covering this.