Grounding Multi-Ratio CTs

Status
Not open for further replies.

Bugman1400

Senior Member
Location
Charlotte, NC
You don't ground polarity. Polarity is the smaller number and goes to the instrument (X1 for your example). The higher of the used numbers gets grounded (X2 for your example).
Whether you ground the polarity side or the non-polarity side is a matter of application. Some devices use the non-polarity instead.....metering comes to mind since many times it uses the opposite side that of the relaying. There is also the off-chance that the CT was incorrectly installed in reverse.
 

mivey

Senior Member
Whether you ground the polarity side or the non-polarity side is a matter of application. Some devices use the non-polarity instead.....metering comes to mind since many times it uses the opposite side that of the relaying. There is also the off-chance that the CT was incorrectly installed in reverse.
True enough.:thumbsup: I was in substation mode.
 

ATSman

ATSman
Location
San Francisco Bay Area
Occupation
Electrical Engineer/ Electrical Testing & Controls
Sunny,

X1-X2 has, say=40 turns; X2-X3=30; X3-X4=20; X4-X5=10! Always maintain the ground-connection at X5! Then, connect burden-devices between X1, and X5!

Thus, Max turns-ratio, available, between X1-X5 is 100:1!

Example 2: you want 50:1 ratio, simply short terminals X2-X3-X4!

Example 3: you want 10:1 ratio, simply short terminals X1-X2-X3-X4!

And, you must never leave turns open-circuited!

Regards, Phil Corso

Phil
Looks like you are thinking of a different device;

http://www.schneider-electric.us/en/faqs/FA111406/
 

rian0201

Senior Member
Location
N/A
You don't ground polarity. Polarity is the smaller number and goes to the instrument (X1 for your example). The higher of the used numbers gets grounded (X2 for your example).

i disagree this depends on your application.. you can ground either X1/X2, in my example, if the use of such CT demands it and as long as you only ground one point..


Sent from my iPad using Tapatalk
 

rian0201

Senior Member
Location
N/A
Whether you ground the polarity side or the non-polarity side is a matter of application. Some devices use the non-polarity instead.....metering comes to mind since many times it uses the opposite side that of the relaying. There is also the off-chance that the CT was incorrectly installed in reverse.

i agree with this


Sent from my iPad using Tapatalk
 