I am looking for the correct NEC section regarding the grounding of an owner supplied 12.47/480 3ph pad mounted transformer and 480v switchboard system.
I am proposing it to be grounded/bonded as per 250.30, using the Exhibit 250.14 in the NEC Handbook, is this correct ?
If not what would be the correct section ?
Is this is correct, can the bonding conductor between the chassis of the switchboard and the case of the transformer be directly encased in the concrete ductbank between the transformer and the switchboard (this is what we have now).
The owner wants us to also provide an additional grounding conductors in the incoming conduits along with the bonding conductor in the ductbank. I feel this is incorret.
Thanks
Tom
I am proposing it to be grounded/bonded as per 250.30, using the Exhibit 250.14 in the NEC Handbook, is this correct ?
If not what would be the correct section ?
Is this is correct, can the bonding conductor between the chassis of the switchboard and the case of the transformer be directly encased in the concrete ductbank between the transformer and the switchboard (this is what we have now).
The owner wants us to also provide an additional grounding conductors in the incoming conduits along with the bonding conductor in the ductbank. I feel this is incorret.
Thanks
Tom