Smart $ said:However, this installation falls under 250.24 (not 250.30) through 250.28.
Smart $, Article 250.30 and 250.24 should get together and unify. There is a difference between the two and that is the point of service.I'll add the quote from the handbook to explain the difference between the two.
handbook said:The power for ac premises wiring systems is either separately derived, in accordance with 250.20(D), or supplied by the service. See the definition of service in Article 100. Section 250.30 covers grounding requirements for separately derived ac systems, and 250.24(A) covers system grounding requirements for service-supplied ac systems.
According to 250.24, a premises wiring system supplied by an ac service that is required to be grounded must have a grounding electrode conductor at each service connected to the grounding electrodes that meets the requirements in Part III of Article 250. Note that the grounding electrode requirements for a grounded separately derived system are specified in 250.30(A)(3), (A)(4), (A)(5), and (A)(7).