Re: Grounding of a satellite dish mast
Pierre,
Good follow-up explanation.
Recently seen a plot with four duplex's ( with about 12 feet between each bldg, in a line along a street. The first and last duplex bldg's had the Electrical Service Entrance (SE) on the far ends of the bldg's and the center two duplex had the SE facing each other across the 12' space. The CATV and the Telephone POE's were on the opposite end of each bldg from the SE. Thus two instances of the CATV and the Telephone POE's were facing each other across the 12' space.
Originally the Telephone drove a 5' Ground Rod for the POE and the CATV which came later drove one Ground rod for each of the face-to-face POE's.
Neither the telephone nor the CATV grounding was acceptable. They, telephone and CATV, finally agreed to use a single ground rod for each of the first two bldg's POE's and install a buried 6 AWG around the rear of each duplex to the SE for the respective duplex.
Then on the second set of duplex's when the CATV came, the installer decided to just bond to the EMT for the Air Conditioner (A/C) which was a about a foot away from the CATV POE. That didn't meet NEC either. They finally meet the NEC 8xx.40 for all four duplex bldg's.
Kept hearing comments similar to " Never had to do that before.".
Pierre,
Good follow-up explanation.
Recently seen a plot with four duplex's ( with about 12 feet between each bldg, in a line along a street. The first and last duplex bldg's had the Electrical Service Entrance (SE) on the far ends of the bldg's and the center two duplex had the SE facing each other across the 12' space. The CATV and the Telephone POE's were on the opposite end of each bldg from the SE. Thus two instances of the CATV and the Telephone POE's were facing each other across the 12' space.
Originally the Telephone drove a 5' Ground Rod for the POE and the CATV which came later drove one Ground rod for each of the face-to-face POE's.
Neither the telephone nor the CATV grounding was acceptable. They, telephone and CATV, finally agreed to use a single ground rod for each of the first two bldg's POE's and install a buried 6 AWG around the rear of each duplex to the SE for the respective duplex.
Then on the second set of duplex's when the CATV came, the installer decided to just bond to the EMT for the Air Conditioner (A/C) which was a about a foot away from the CATV POE. That didn't meet NEC either. They finally meet the NEC 8xx.40 for all four duplex bldg's.
Kept hearing comments similar to " Never had to do that before.".