@jaggedben reply he answered well with relevant questions
"Service Conductors" are not "Feeders":
The two terms are mutually exclusive. You cannot apply Feeder rules (like EGC sizing) to Service Conductors:
* NEC Definition (Article 100) - Service Conductors: "The conductors from the service point to the service disconnecting means."
* NEC Definition (Article 100) - Feeder: "All circuit conductors between the service equipment... and the final branch-circuit overcurrent device."
If these conductors are upstream of the main disconnect, they are Service Conductors. Therefore, they do not utilize an "Equipment Grounding Conductor" (EGC). They utilize a Supply-Side Bonding Jumper (SSBJ).
"Three Loads" are not "Parallel":
If the installation feeds three separate loads, these are three separate circuits. They are not "parallel conductors.":
* 310.10(G) (formerly 310.10(H)) - Conductors in Parallel: This section explicitly requires parallel conductors to be "electrically joined at both ends."
If these runs go to three different loads, they are not joined at the load end. Therefore, they are Multiple Circuits, not Parallel Conductors. And if I'm reading you correctly "medium voltage switchgear" the three TX land there is where your OCPD will most likely be and the "Service Conductors" end there and they become feeders to the final OCPD at these three loads. So you need a EGC for each of those three in this case'
Hope this helps'