Re: Grounding of Surge Arresters and TVSSs
Since all you asked about was the ground connections I will limit myself just to that subject (hard to do). Ground has no purpose in a service entrance TVSS device other than that of any other EGC. It is just there to provide a fault path in case of accidental faults from phase to ground?.. So run your EGC with line and neutral conductors as closely grouped as possible. Use cable ties to keep grouped tightly.
There are two very good reasons why I say this.
1. According to ANSI/IEEE C62.45, 95% of all lightning strikes occur ahead of the transformer primary or input side. This means the surge on the output side of the transformer will be in the differential mode meaning between L-N on grounded systems, and L-L on un-grounded systems. This is as opposed to common mode from L-G. Any transformer provides very good Common Mode Rejection or common mode TVSS, but no differential mode protection.
2. If you do not believe #1 then consider this. At the service entrance what is the grounded conductor connected too? Hint, I will not spell it out but some of the initials are GEC or MBJ. With that in mind comes the next point.
At the service entrance there is no need for ?all mode? protector modules. All modes protectors are L-L, L-G, L-N, and N-G. All that is needed is L-N. All other modes are redundant and add extra cost. Best buy and maximum protection is L-N models with the largest modules you can afford. You can also apply this same principle to any class B devices downstream from service entrance at the output of step-down or isolation transformers for the reasons already given.
Down stream devices at sub-panels can benefit from all mode devices, but you run the ground with line and neutral conductors as you normally would. If you insist on adding an external ground to the electrode system do it from the sub-panel ground bus rather than the TVSS all mode device.
[ September 12, 2003, 11:32 PM: Message edited by: dereckbc ]