We are trying to make safe electrical installations on grounding issues.....some body has put ground rods at the generator and all the sub-panels following. I am thinking that multiple ground rods at various locations create a danger in itself as the difference of potential between ground rods may induce a current on the grounding path.
To clarify the installation:
We have 2 120kw generators connected to a main transfer switch which also breaks the neutral, to a main distribution panel which feeds various sub-panels located thru-out the compound.
Should we disconnect all the ground rods at the subpanels and make all the fault current return to the source via the equipment grounding conductor?
Thanks for the help!