Grounding on Transformer Primary Side

Status
Not open for further replies.

samcon

Member
I have an unusual situation, at least for me. I have to provde a temporary service to an office trailer, which involves running 480V., 80A. single phase from a panel in a building a distance of 1250' underground to the trailer. I am going to use direct burial single conductor 4/0 aluminum to keep the cost down. At the trailer I will use a transformer to step it down to 120/240 single phase. My main question is: do I need to run a ground wire with the primary phase conductors from the building to the trailer? I don't believe it is necessary since I will be creating a neutral at the trailer by bonding XO to the frame of the trailer, and driving a ground rod which will, I believe, also be connected at XO (correct me if I'm wrong). Any input on this matter would be greatly appreciated.
 

iwire

Moderator
Staff member
Location
Massachusetts
samcon said:
My main question is: do I need to run a ground wire with the primary phase conductors from the building to the trailer?

Yes, you must bring a grounding means with the circuit conductors from the source and connect it to the transformer enclosure.

I don't believe it is necessary since I will be creating a neutral at the trailer by bonding XO to the frame of the trailer, and driving a ground rod which will, I believe, also be connected at XO

It is still necessary, all the work you describe only provides protection for faults on the secondary side of the transformer.

The EGC you must run from the source is to protect against primary side faults. As in a primary winding to case fault.
 

tom baker

First Chief Moderator
Staff member
Samcom, on the primary side you need an EQC so in the event of a line to case fault on the primary side the fault current can return to its source. The secondary has a system bonding jumper, for return of secondary fault current to its source, the transformer.
 