kwired
Electron manager
- Location
- NE Nebraska
- Occupation
- EC
The main bonding jumper cannot be in the wireway, See 250.24(B). I think that section requires the main bonding jumper to be in the service enclosures. It is true that the GEC can be connected to the grounded conductor in the wireway, but that does not constitute the main bonding jumper. The main bonding jumper's purpose is to connect the grounded conductor to the equipment grounding conductors and the service enclosure.
I agree with you on this.
What is your view on the "taps" that is mentioned in the OP? I feel they are pointless if installed in a manner that creates a parallel path with the grounded service conductor. They would also violate many of the requirements of 310.4.