If I have a 200 amp panel and run a sub panel to my barn 100 A
Does that panel have to have a ground rod?
If yes where is that in code
]
 
Why yes I am Terry, and the others are correct.

Was there a problem with my answer in your oppinion?

Roger
 
mdshunk said:
Some of us might have even Google'd his user name. Holy smokes! :-?

Now that's downright frightning!!!
speechless-smiley-040.gif



Roger
 
As a matter of fact I did I always do. I did not google him though I knew MD would do that.

I am glad he was not my electrical (instructor). I believe all I enter into profiles but sometimes am skeptical about others. I guess I better go talk to my shrink. I'm apparently having some thinking problems.

Sorry having a bad day! My apologies.
 
You need to ground as if it is a feeder! 250.32.

250.32 Buildings or Structures Supplied by Feeder(s) or
Branch Circuit(s).
(A) Grounding Electrode. Building(s) or structure(s) supplied
by feeder(s) or branch circuit(s) shall have a grounding
electrode or grounding electrode system installed in
accordance with 250.50. The grounding electrode conductor(
s) shall be connected in accordance with 250.32(B) or
(C). Where there is no existing grounding electrode, the
grounding electrode(s) required in 250.50 shall be installed.

There is an excellent graphic on this subject here on this site. Just search and you will find it or someone else can probably give you the link. I can't seem to find it at this time. If you pm me I can email it to you as I have it on my hd.
 
Terrynistler said:
You need to ground as if it is a feeder! 250.32.

With no more information given how do you know it can't be grounded as if it were a service?

Roger
 
mrj77511 said:
If I have a 200 amp panel and run a sub panel to my barn 100 A
Does that panel have to have a ground rod?
If yes where is that in code
]


You got me I guess I haven't seen any barns attached to houses here in texas. What is he going to his barn from? I was agreeing with you just supplying the text from the NEC.
 