I'm designing a 13.8kV switchgear building at a hospital. The gear will be owned by the customer and contain utility primary metering in it. This switchgear will feed existing pad mounted transformers which then in turn feed existing hospital 480V distribution system, etc.
Into this building, I need to bring a 480V service for lights, receptacles, a heat pump for heating and cooling the building and various sundry things.
I know that when I bring a service like this to another building to provide a ground rod for that service but not to bond the neutral to ground at that point.
I also will be providing a triplexed ground rod system for grounding of the 13.8kV incommingt service. For this I'm employing a grounding bar on the interior wall of the building.
Here's the big question, do I connect my grounding electrode system for the low voltage system to my grounding electrode system for the medium voltage system.
On the one I am concerned that if I don't do it, I could create a situation where there are two potentials on two separate grounding systems.
On the other hand, I wouldn't normally connect the grounding system from the dela side of my transformers to my service grounding electrode system.
Not sure what to do?
Thanks,
Mike
Into this building, I need to bring a 480V service for lights, receptacles, a heat pump for heating and cooling the building and various sundry things.
I know that when I bring a service like this to another building to provide a ground rod for that service but not to bond the neutral to ground at that point.
I also will be providing a triplexed ground rod system for grounding of the 13.8kV incommingt service. For this I'm employing a grounding bar on the interior wall of the building.
Here's the big question, do I connect my grounding electrode system for the low voltage system to my grounding electrode system for the medium voltage system.
On the one I am concerned that if I don't do it, I could create a situation where there are two potentials on two separate grounding systems.
On the other hand, I wouldn't normally connect the grounding system from the dela side of my transformers to my service grounding electrode system.
Not sure what to do?
Thanks,
Mike