Is grounding required on a 240v to 120v control transformer where the primary is single phase of a 3 phase 120/240 high leg delta. Does it make a difference if the high leg is used or not.
The way I read it if, there is greater than 150volts to ground on any of the primary conductors (the high leg would qualify, but not the others) then groundig of the secondary is required.