The only correct place to take the test is at the UUT (Unit Under Test), or at the rod with it disconnected from the AC system or anything else. It's not 75, but 25 or less.Originally posted by royboy:
To settle a bet. Where is the best place to take your ohmmeter measurements from for the 75 ohm reading? If not 75 or less install another ground rod within 6 feet correct?
Probable when an impedance is specified in contract obligations, otherwise inspector's judgement. In all my applications, which is telecom, 5 ohm's or less as measured with "Fall-Of-Potential" method.Originally posted by speedypetey:
While we are on this subject, how many of you have actually checked the resistance of a ground rod?
Pierre, I was referring too a 3-point "Fall-of-Potential" test method.Originally posted by pierre:
The grounding system does not have to be disconnected Pierre
Unless the fuse was very small, I doubt any fuse would operate, ground resistance is too high to carry enough fault current to operate a OCPD. However I have seen and heard of this method used as a "poor man's" method of measuring ground resistance.Originally posted by caosesvida:
my father told me they used to hook the ground rod to a fuse and put a small amp fuse in and see if it would fail. If not they would supplement the ground rod.