T thewire Member Location Raleigh Mar 12, 2021 #1 Is there a min distance separation from the grounding grid/ring from the cabinet/house? You have the cabinet/house siting in the middle with the ground rods on all corners of the cabinet/house. The cabinet is bonded to the grounding grid/ring
Is there a min distance separation from the grounding grid/ring from the cabinet/house? You have the cabinet/house siting in the middle with the ground rods on all corners of the cabinet/house. The cabinet is bonded to the grounding grid/ring
tom baker First Chief Moderator & NEC Expert Staff member Location Bremerton, Washington Occupation Master Electrician Mar 12, 2021 #2 No, the requirements are the ground ring must be a minimum of 20 feet long, 30 inches deep, 2 awg min.
No, the requirements are the ground ring must be a minimum of 20 feet long, 30 inches deep, 2 awg min.