Grounding rod bonding to water pipe??

Status
Not open for further replies.

Toros

Senior Member
Location
Tujunga, CA
Hi,
I am installing a supplemental copper rod at existing 1200A, 3-ph. service that has only grounding system electrode/conductor to the main water pipe. now, Can I connect the GEC from the new grounding ro to the same main water pipe where other one is already connected;
or I have to run it all the way to grounding/neutral bus of the existing service??????

Thank you
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
If you connect between the existing connection and where the pipe enters the earth, you will be connecting to the existing electrode, which is allowed.


Tapatalk...
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
All electrodes are permitted to be joined together to form the GES or grounding electrode system with bonding jumpers.

1113918256_2.jpg
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
In most cases the connection would have to be to the water pipe within 5' of where the water pipe enters the building.
 