Correct. You also need separate grounded and equipment grounding conductors beyond the system bonding point, which is likely going to be within the transformer housing on this one. So even if a fuse would happen to blow within appliance in the grounded conductor it isn't really that dangerous of an issue to the user, might be more risk to someone troubleshooting problems that don't understand what they have to work with.
"
So even if a fuse would happen to blow within appliance in the grounded conductor it isn't really that dangerous of an issue to the user,"
Because the OP has abandoned he his own thread we are left with only assumptions. We do not have any information, electrical specs, on the
cooking appliance". All we have to work with is a 1ph 480V to 208V 30KVA transformer.
Assume this cooking appliance/equipment will be hard wired. (High probability)
The NEC says it shall Listed. Lets assume the appliance is UL Listed.
Lets assume both 208V lines feeding heating elements are individually fused.
If one leg of the transformer's secondary is grounded, making it the grounded conductor, the grounded conductor will be fused feeding one end of each connected heating element. Do you think the designer of the appliance/equipment would sign off on that? Would UL? Would it void the UL listing? Would it void the manufacturers' warranty?
If you pulled an electrical permit would the electrical inspector agree with your statement, "
So even if a fuse would happen to blow within appliance in the grounded conductor it isn't really that dangerous of an issue to the user," and pass the inspection?
If it were me I would call the manufacturer of the cooking appliance before I proceeded doing anything that involved using the transformer in question.
.