Re: Grounding Separately Derivied Systems Article 250.30
KQRESQ, what would be wrong with running the GEC to the transformer with the primary phase conductors as long as it is sized per 250.66 for the derived secondary conductors, and terminated to the Xo? You could use the metalic raceway as the EGC for the primary protection.
Provided the GEC is bonded to the metalic raceway at each end, I cannot see how that would be a problem with the code as long as it originated from the service.
KQRESQ, what would be wrong with running the GEC to the transformer with the primary phase conductors as long as it is sized per 250.66 for the derived secondary conductors, and terminated to the Xo? You could use the metalic raceway as the EGC for the primary protection.
Provided the GEC is bonded to the metalic raceway at each end, I cannot see how that would be a problem with the code as long as it originated from the service.