ty
- 3rd Rock from the Sun
To comply with 250.148, the easiest way would be with a ground bus connected to the metal box.
You could not just wirenut the equipment grounding conductor to just its mate. You would need to splice ALL the equipment grounds together and then make a connection to the box.
Chris
I do not agree. I do not read the wording to say that.
250.148 does Not say 'they shall be connected together', it also says 'any' not 'ALL'.
If you were to bring 12/2 into a 2-gang Plastic box for a receptacle, and 14/2 into the same box for a switch, I do not read that to say all EGC's need to be connected togeter. In a metal box, they would be by default.