LECTRICBOSS
Member
- Location
- MOORE, OK. USA
THE ENGINEER SHOWS US TO PROVIDE A 2,500 AMP MAIN DISCONNECT ON THE EXTERIOR OF THE BUILDING AND A 2,500 AMP MAIN DISTRIBUTION PANEL ON THE INTERIOR OF THE BUILDING WITH A MAIN CIRCUIT BREAKER. THEY SHOW NO GROUNDING DONE AT THE MAIN SWITCH BUT ALL OUR GROUNDING DONE AT THE MAIN DISTRIBUTION. THEY ALSO SHOW NO GROUNDING CONDUCTOR INSTALLED IN THE CONDUITS FROM THE UTILITY TRANSFORMER (I AGREE) AND NO GROUNDING CONDUCTORS INSTALLED FROM THE MAIN SWITCH TO THE MAIN DISTRIBUTION (I DISAGREE). I BELIEVE ACCORDING TO THE 2011 CODE SECTION 250.24 APPLIES HERE. I HAVE QUESTIONED THE ENGINEER ABOUT JUST DOING AWAY WITH THE MAIN SWITCH AS WE HAVE A MAIN IN OUR MDP BUT THEY SAY THE UTILITY REQUIRES THIS. I AM NOT SURE BUT I BELIEVE WE ARE NOT COMPLYING WITH THE CODE HERE. PLEASE SEND COMMENTS. THANKS.