Grounding subpanel

Status
Not open for further replies.

Cavie

Senior Member
Location
SW Florida
I think I saw a thread about this last week but can't remember. Is it ok to ufer ground a subpanel along with the main panel ufer? this may be a second post. I could not find the first one.
 
You can add any supplemental ground you want to branch panels. They just cannot be used in lieu of the EGC requirements from the supply panel.
 
Cavie said:
I think I saw a thread about this last week but can't remember. Is it ok to ufer ground a subpanel along with the main panel ufer? this may be a second post. I could not find the first one.

My question would be , why would you want to supliment the grounding conductor ????? The sub panel already has a seperate grounded and grounding conductor.Or are you asking if you can use the ufer and run a 3 wire to the sub from the supply/main panel ???
 
ramdiesel3500 said:
I must have missed something recently. What does "ufer" mean???

Many people call an NEC concrete encased electrode a 'uffer'

This is because Herbert G. Ufer did a lot of work with concrete encased electrodes. He was trying to ground buildings that contained munitions during WWII.

From what I have read Ufer's concrete encased electrodes where more elaborate than what the NEC requires.
 
the guy rand a 4 wire to the subpanel but for some reason I don't know, the is a # 10 insulated green run in the wall to the footer steel.
 
Cavie said:
the guy rand a 4 wire to the subpanel but for some reason I don't know, the is a # 10 insulated green run in the wall to the footer steel.
Maybe the #10 was installed first, and later the correction was made.
 
iwire said:
Many people call an NEC concrete encased electrode a 'uffer'

This is because Herbert G. Ufer did a lot of work with concrete encased electrodes. He was trying to ground buildings that contained munitions during WWII.

From what I have read Ufer's concrete encased electrodes where more elaborate than what the NEC requires.


I agree, although we seem to use the terms Ufer and CEE interchangeably there is quite a difference between the two. The Ufer is far more elaborate.
 