hardworkingstiff said:
Kids are gone, one of them has my grandson. Been just my and my wife for quite a few years (my last one [son] basically wasn't here the last 3 years he lived with us and he's been gone for 2 years).
Okay, let me try again.

Ever had a kid misbehave to the point they were not allowed to go anywhere for a week or so?
 
Wow. Grounding wasn't an option in Lou's house, ey... :shock:

cat%20o%20nine%20tails.jpg
 
Escapades said:
Is it required to ground all light switches in residential construction?

Mike

Back to the OP. Yes grounding is required. A plastic box will require an EGC connection to the switch. A metal box will require nothing, since the 6/32 screws will ground the switch.
 
infinity said:
Back to the OP. Yes grounding is required. A plastic box will require an EGC connection to the switch. A metal box will require nothing, since the 6/32 screws will ground the switch.

Only if self grounding,not all will be.
 
Jim,
Only if self grounding,not all will be.
The code says that all you need to bond a switch to a metal box is the switch mounting screws.
404.9(B) Grounding Snap switches, including dimmer and similar control switches, shall be effectively grounded and shall provide a means to ground metal faceplates, whether or not a metal faceplate is installed. Snap switches shall be considered effectively grounded if either of the following conditions is met:
(1) The switch is mounted with metal screws to a metal box or to a nonmetallic box with integral means for grounding devices.
(2) An equipment grounding conductor or equipment bonding jumper is connected to an equipment grounding termination of the snap switch.
Don
 
Jim W in Tampa said:
Only if self grounding,not all will be.


As Don posted, switches do not need to be self-grounding. The use of a metal box in combination with the metal mounting screws satisfies the switch bonding requirement.
 
so if the switch has a ground screw I can just ignor it because it was put there for decoration and to add a little color to the other screws on the switch
You can ignor it only if you are installing the switch in a grounded metal box. The screw is there for when you install the switch in a non-metallic box.
Don
 
marinesgt0411 said:
so if the switch has a ground screw I can just ignor it because it was put there for decoration and to add a little color to the other screws on the switch
We bond to a ground screw in a metal box AND to the screw on the device - local code. But then again, we pull a green in metal conduit too. Oklahoma City is serious about grounding.
 
marinesgt0411 said:
so if the switch has a ground screw I can just ignor it because it was put there for decoration and to add a little color to the other screws on the switch
Just like ignoring the second brass and silver screws on a duplex that happens to be the last (or only) receptacle on a line.
 