Our community wants to provide temporary load centers for downtown events such as parades and festival events. These would be 100 amp panels set up on portable stands, fed with 4-wire assemblies and intended to be plugged into a permanently installed receptacle for power. Would each of this locations be required to establish a new grounding electrode system or is the 4-wire adequate for grounding. All of them will originate from a main panel location. Since each of this portable panels could be considered a separate structure I am thinking an electrode system might be required a each location. Still in preliminary design but requesting any thoughts.
I think "Dirt worshiping 101, is typically first training inspectors get on their way to inspector certification.Late to the party...
The film and live events industry would grind to an absolute halt if we were required to drive a ground rod(s) at every spider box and cord-and-plug-connected temp panel. The ground would look like Swiss cheese. The only time ground rods are ever driven (and even then, not always) is when portable generators are used. The neutral and ground are bonded at the genny, and a ground rod is whacked into some patch of earth to keep the fire marshal and the dirt worshipers happy. The justification I've heard is... lightning strikes... nothing's gonna save your gear if a bolt from above hits your install directly, ground rod or not.
I wouldn't worry about driving a rod(s) for a temp panel as described, so long as the feed to it were 4-wire (or 5-wire, if three-phase). The neutral and ground buses would of course have to be separated, and the panel treated as a subpanel.
SceneryDriver
I think "Dirt worshiping 101, is typically first training inspectors get on their way to inspector certification.
They don't even have to pay for that course, it is just given to them by inspector unions, associations, or whatever they belong to.
"I never go anywhere without a ground rod and a driver in my trunk just in case"
First please do not drive ground rod. ... Just trying to help.