DMSatinstaller
Over the past month, I have seen two new homes that have the #6 ground wire from the electrical service panel connected to the incoming Natural Gas line to the home. Is this acceptable?
DMSatinstaller said:Over the past month, I have seen two new homes that have the #6 ground wire from the electrical service panel connected to the incoming Natural Gas line to the home. Is this acceptable?
No, an underground metal gas line cannot be used as a grounding electrode.DMSatinstaller said:Is it acceptable in lieu of a ground rod? Neither of these instances had ground rods installed.
yanici said:For what it's worth, I've read on the forums that the gas utility installs a dielectric fitting on the gas service to the building to act as an insulator. That way the underground pipe can't act as an electrode. my 2cents. (sorry winnie, I type slow)
barbeer said:I prefer to see the circuit feeding the equipment connected to gas to provide the bond (EGC) as the NEC dictates is acceptable.
JohnJ0906 said:So do I. However, some jurisdictions here are now requiring a separate bond for gastite flex systems.
raider1 said:This is actually a manufacturers requirement for Gastite brand CSST.
Chris
stickboy1375 said:But probably a manufactures Lawyers requirement... :grin: