I'm upgrading my GEC because the current one that was installed before I bought my house is undersized and they used THHN stranded wire run underground to the ground rod in EMT. I dug it up last night and there wasn't much of the EMT left.
I now have added another ground rod about 12' apart from the other one connected together in series by a #4 bare copper and I'm running a #4 bare wire to were my copper water main comes into the house to my service . The previous GEC from the ground rod was connected at the meter, but wouldn't connecting it at the service be a better option? Let's just say you don't have the option of a water line and the neutral for some reason becomes loose or breaks between the service and the meter. Wouldn't having the ground rod connected in the meter be useless if you lost that conductor in that situation? Where would your path to ground be since it was dependent on the neutral wire? I'm just trying to make this the safest system that I can.
Or maybe I'm over thinking this
Thanks
Ben
I now have added another ground rod about 12' apart from the other one connected together in series by a #4 bare copper and I'm running a #4 bare wire to were my copper water main comes into the house to my service . The previous GEC from the ground rod was connected at the meter, but wouldn't connecting it at the service be a better option? Let's just say you don't have the option of a water line and the neutral for some reason becomes loose or breaks between the service and the meter. Wouldn't having the ground rod connected in the meter be useless if you lost that conductor in that situation? Where would your path to ground be since it was dependent on the neutral wire? I'm just trying to make this the safest system that I can.
Or maybe I'm over thinking this
Thanks
Ben