Re: Grounding vs. Bonding - difference
"So then the EGC is not intended to bond the components to earth but to provide an alternate low impedence path"
This is important.
Not an alternate path
But the path. Look at the defintion of the effective ground fault current path in 250, and the ground fault current path. The first is the one we make, the second is the one the fault current takes....
"So then the EGC is not intended to bond the components to earth but to provide an alternate low impedence path"
This is important.
Not an alternate path
But the path. Look at the defintion of the effective ground fault current path in 250, and the ground fault current path. The first is the one we make, the second is the one the fault current takes....