grounding wire size to VFD input

Merry Christmas

TMMB

Senior Member
Location
EGYPT
Occupation
Electrical Manager
I would like to know how i can sizing the grounding wire conductors included in VFD cables, the cable is 6 cores, 3 for power & another 3 for grounding
how I can sizing the grounding wires
 
Not sure I'm getting the question right. What is the size of the drive? What amperage is it rated for? If such wires are included, what size are they now?
 
Not something we typically use here in the US but permitted by the NEC.

250.122 Size of Equipment Grounding Conductors.
250.122(A) General.
Copper, aluminum, or copper-clad aluminum equipment grounding conductors of the wire type shall not be smaller than shown in Table 250.122. The equipment grounding conductor shall not be required to be larger than the circuit conductors supplying the equipment. If a cable tray, a raceway, or a cable armor or sheath is used as the equipment grounding conductor, as provided in 250.118 and 250.134(1), it shall comply with 250.4(A)(5) or (B)(4). Equipment grounding conductors shall be permitted to be sectioned within a multiconductor cable, provided the combined circular mil area complies with Table 250.122.
 
Not sure I'm getting the question right. What is the size of the drive? What amperage is it rated for? If such wires are included, what size are they now?
VFD drive for motor 60 HP, 400V, 3 Ph , the VFD cable (6 cores), 3 for power and 3 for grounding
i Know how to size the 3 core of the power, my Q is , how to size the 3 cores of the grounding
 
VFD drive for motor 60 HP, 400V, 3 Ph , the VFD cable (6 cores), 3 for power and 3 for grounding
i Know how to size the 3 core of the power, my Q is , how to size the 3 cores of the grounding
The answer is in the code section in post #5.
 