An easier and cheaper solution is a non insulated fork terminal. The insulated ones are hard to crimp without a good tool. I make up a bunch of 12 AWG pigtails with the crimp on terminalspaul said:I find these to be quite useful.
![]()
ibew441dc said:roger
Define grounding screw. I see no spot that says it has to be approved.
Also check out 250.8 , that should clear it up.
What do ya think?:smile:
roger said:I know what the article says, maybe this will help you.
![]()
The termination of equipment grounding and bonding conductors must be by exothermic welding, listed pressure connectors of the set screw or compression type, listed clamps, or other listed fittings. Sheet-metal screws cannot be used to connect grounding (earthing) or bonding conductors or connection devices to enclosures. Figure 250?42
Author?s Comment: The rule still doesn?t prohibit drywall screws or wood screws from being used for this purpose, just ?sheet-metal? screws!
Roger
tbonse said:Yes, It may not specifically prohibit drywall or wood screws, but as they're not UL listed for electrical bonding, they're also not permitted. :grin: