grounding with brass screws

Status
Not open for further replies.

jb64

Member
Location
Warwick, RI
I am an electro-mechanical technician who builds and wires industrial assembly machinery. Recently, I was told that when I install the ground lug on the power panel that I am required to use a brass screw. Also I scrape the paint off of the panel so that the ground lug is against the bare metal. This same person says that is unnecessary as the screw makes the ground. I disagree with him but I have found nothing in the NEC to affirm or refute my position. Is my colleague right?
 
Re: grounding with brass screws

jb64 said:
I am an electro-mechanical technician who builds and wires industrial assembly machinery. Recently, I was told that when I install the ground lug on the power panel that I am required to use a brass screw. Also I scrape the paint off of the panel so that the ground lug is against the bare metal. This same person says that is unnecessary as the screw makes the ground. I disagree with him but I have found nothing in the NEC to affirm or refute my position. Is my colleague right?

On scraping part yes but know of no reason for brass screws.
 
See NEC 250.12 This is generally read as requiring the removal of paint from _contact surfaces_, or require the use of fittings that make the removal of paint unnecessary.

A common fitting used to make paint scraping unnecessary is a 'paint piercing grounding washer'.

Most 'grounding screws' (eg. those used in junction boxes) are simply green screws with a head that grips wire well, probably steel.

-Jon
 
Re: grounding with brass screws

Jim W in Tampa said:
jb64 said:
I am an electro-mechanical technician who builds and wires industrial assembly machinery. Recently, I was told that when I install the ground lug on the power panel that I am required to use a brass screw. Also I scrape the paint off of the panel so that the ground lug is against the bare metal. This same person says that is unnecessary as the screw makes the ground. I disagree with him but I have found nothing in the NEC to affirm or refute my position. Is my colleague right?

On scraping part yes but know of no reason for brass screws.

I think Jim meant you are right on scraping part; not your colleague.

I also agree with Jon on 250.12. And if you are not tapping that hole there is absolutely no doubt about it: unless using fitting designed for the purpose you must scrape the paint.
 
Re: grounding with brass screws

jb64 said:
I am an electro-mechanical technician who builds and wires industrial assembly machinery.

The NEC may not apply.

It sounds like NFPA 79 Electrical Standard for Industrial Machinery would be the correct standard.
 
Re: grounding with brass screws

iwire said:
The NEC may not apply.

It sounds like NFPA 79 Electrical Standard for Industrial Machinery would be the correct standard.

I was thinking along the same lines.
 