Grounding Xfrmr

Status
Not open for further replies.

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
I am replacing about (10) 45 and 75kva xfrms. Within electrical closets. There are no grounding details just a note to ground per NEC 250. This is very vague and not sure how to approach pricing up grounding. I guess I can take to a ground bar in the room or building steel in the room? Since there are not detail I would qualify grounding limited to the room and not beyond.
 
I am replacing about (10) 45 and 75kva xfrms. Within electrical closets. There are no grounding details just a note to ground per NEC 250. This is very vague and not sure how to approach pricing up grounding. I guess I can take to a ground bar in the room or building steel in the room? Since there are not detail I would qualify grounding limited to the room and not beyond.
Since you are replacing transformers, why wouldn't your clarification be "reuse existing ground only."
 
Is this a steel famed building? If so just run the GEC's to the nearest building steel. If all 10 transformers are in the same room you could install a ground bar.
 
I am replacing about (10) 45 and 75kva xfrms. Within electrical closets. There are no grounding details just a note to ground per NEC 250. This is very vague and not sure how to approach pricing up grounding. I guess I can take to a ground bar in the room or building steel in the room? Since there are not detail I would qualify grounding limited to the room and not beyond.
The reference to Article 250 will require you to provide a connection to a grounding electrode per the requirements for separately derived systems...250.30
 