Grounding

Status
Not open for further replies.

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
Does a panelboard need to be tied into(separate conduit and wire) a separate grounding system? Doesn't the conduit provided grounding and bonding?
 
A panel is grounded by the connection to the EGC run with the feeder. It could be a metal raceway, wire type EGC, or both.
 
The code is very specific about this. The equipment grounding conductor must be run with the circuit conductors. It cannot be separate.
 