Re: Grounding
Actually Bennie is correct. Here is the NEC language for receptacle grounding
405.3 (B) To Be Grounded. Receptacles and cord connectors that have grounding contacts shall have those contacts effectively grounded.
The definition of effectively grounded is
Grounded, Effectively. Intentionally connected to earth through a ground connection.
Dirt is then an allowed method.
This is exactly why Don G (Moderator) made many proposal to change equipment grounding conductor to equipment bonding conductor.
Lightbugg-The nec has allowed methods for installing an equipment grounding conductor, see 250.130(C).
The most cost effective method is to replace the two wire receptacle with a GFCI. See section 406.3