If you have a feed through panel on a pole and you want to pull power wires to a house, garage, and barn do you need to pull a ground wire with all them or can you use ground rods at each location?
 
Re: Grounding

No, this is permitted as long as there is no metal connection between the two buildings that could act as a parrallel path for nuetral current, at the house, barn, garage you would bond all GEs to make up the GE System

[ January 05, 2006, 02:47 PM: Message edited by: Jhr ]
 
Re: Grounding

BTW, regardless of whether or not you pull an equipment ground to the separate locations, 250.32 will require ground rods or some other grounding electrode at each building.
 