Home inspector says this is not allowed: ground and neutral under the same screw in neutral busbar in panel. The whole panel is this way. My worker says each ground/neutral wire is from the same circuit. Is this allowed ? Thank you.
 

tom baker

First Chief Moderator
Staff member
This was a violation when installed, HI is correct, this was a UL requirement, and since so few knew it, it was added to the NEC many cycles ago. You can have 2 EGC under a terminal, but only one neutral under a terminal.
See Section 408.41, for grounded conductor. The EGC (not ground) can have more than one EGC per terminal per mfgs instructions see 110.3B
And ask yourself why this rule exists (hint - keeps the smoke from being let out)
Edited post...thanks Curt
 
Last edited:

curt swartz

Electrical Contractor - San Jose, CA
Location
San Jose, CA
Occupation
Electrical Contractor
HI is correct, this was a UL requirement, and since so few knew it, it was added to the NEC many cycles ago. You can have 2 EGC under a terminal, but only one neutral under a terminal.
At the moment I can't find the code section
And ask yourself why this rule exists (hint - keeps the smoke from being let out)
408.41
 