Does anyone have any insight or knowledge on what the purpose of running a neutral or grounded conductor to the AC side of a GTI is? Some dont require, others do, some manufacturers' inverters can operate without but they seem to strongly prefer that you run one. Whats the deal? I am working on a 1 MW system now and it was designed with full size neutral on the inverter output circuits (3 Ph 480) and a two sized reduced on the feeder to the panelboards. Some of these runs are long so a few are parallel 250 ungrounded conductors for VD. Could some wire have been saved here? These are SMA tripower 24000.