I am putting 6-750KCM conductors in cable tray for 480 volt, 2 A-phase 2 B-phase 2 C-phase

When laid in the tray how should I group in order to avoid EMF problems

AA-BB-CC?

OR

ABC-ABC?
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
The closer the current carrying wires are, in particular the smaller the area that is needed to enclose each balanced group of current carrying conductors, the lower the radiated EMF will be.
So the answer is ABC, ABC. Or, when appropriate, ABCN, ABCN.
And it would be better to lay and tie each three phase group in a triangle rather than in a row flat on the bottom of the tray.
 

dm9289

Industrial Maintenance Electrician
Location
Pennsylvania
Occupation
Industrial process repair/ maintenance Electrician
Thank you

Thank you

Thank you very much, particularly for the triangle hint. I had some related tray cable question today and got no replies at least I now know I am signed in properly.
 